#215635 - 06/16/15 07:23 PM Multiple Tap Connector
brsele Offline
Member
Registered: 07/29/08
Posts: 88
Loc: Northern Ontario
Is anybody from Canada familiar with something like this...

http://ecat.burndy.com:80/Comergent/en/U...ID=BIBD2%2F04MT

If so, do they have to be installed inside a box? Or can you terminate two cables into one? Say to transition from Aluminum to Copper in a tight space.

Thanks
Top
Tools for Electricians:
#215636 - 06/16/15 10:20 PM Re: Multiple Tap Connector [Re: brsele]
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
They have to be inside a box but I've only used them for a temporary connection to bypass a switch, which was outside a box.
Top
#215639 - 06/17/15 06:21 PM Re: Multiple Tap Connector [Re: brsele]
brsele Offline
Member
Registered: 07/29/08
Posts: 88
Loc: Northern Ontario
Thanks, that's what I thought.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals