0 members (), 113 guests, and 10 robots.
I think they really want us to use T/R for all 15 and 20a 120v receptacles.
BigB Offline OP
Not according to 406.12 exceptions 1-4. (2011)
Originally Posted by HotLine1
OK, someone has the '14 changes??
Below is from the 2014 DRAFT...
406.12 Tamper Resistant Receptacles. [ROP 18–41a]
(A) Dwelling Units. In all areas specified in 210.52, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
(B) Guest Rooms and Guest Suites of Hotels and Motels. All nonlocking-type 125-volt, 15- and 20-ampere receptacles located in guest rooms and guest suites of hotels and motels shall be listed tamper-resistant receptacles.
(C) Child Care Facilities. In all child care facilities, all nonlocking-type 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Exception to (A), (B), and (C): Receptacles in the following locations shall not be required to be tamper-resistant:
(1) Receptacles located more than 1.7 m (5 1⁄2 ft) above the floor.
(2) Receptacles that are part of a luminaire or appliance.
(3) A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected
in accordance with 400.7(A)(6), (A)(7), or (A)(8).
(4) Nongrounding receptacles used for replacements as permitted in 406.4(D)(2)(a).
I only carry TR receptacles on my truck these days...
The final text of the 2014 NEC reads exactly the way that shortcircuit posted for 406.12.
Ghost307
BigB Offline OP
I don't see any different wording in the 2014 that's not in the 2011. 406.13 and 406.14 in the 2011 are moved under 406.12 as (B) and (C) in the 2014, word for word.
Yep.
They took out the reference to 'dwelling units' in the Section heading and added 'hotels and motels' to 406.12B and moved a few things around.
Other than that it's the same as it was in 2011.
Ghost307