My anecdote, There was an FP 2 pole disconnect on my water heater and when I was replacing the heater and moving it, I intentionally jumpered out the top thermostat so both eleemts came on, The breaker tripped in a couple seconds. I replaced it with a regular disconnect with the on off handle on the side.
Nah ... I'm looking forward to the next 'ground up vs ground down' thread laugh
IIRC, back in the '70s, My Father told me of the FPE loss of UL listing, with the 50/2 Stab-Lok Devices being specifically noted.
I do not remember if these were the Full-Size Frames (1" per pole), or the "Slim" Frames (1/2" per pole).
Nevertheless, and as mentioned previously, the site of any FPE (Federal Pacific Electric) Device and/or Panelboard should not be cause for Alarm.
As with any other Manufacturer's Product Line, consider replacement if there is an apparent issue with the Equipment.
Issues would include:
A. Inadequate Capacity of Panelboard,
B. Damaged Equipment,
C. Replacement of Panelboard + Devices being more cost effective than obtaining OEM Devices,
D. Device Malfunction - i.e.:
1.: No trip during extended Overload (> 1.5x OCPD trip rating)
2.: Contacts Failure (AKA "Welded Closed")
BTW: No trip during Ground Fault or Short Circuit (L-N or L-L Fault) is not indicative of Device Failure!
When Devices having the same Time Trip-Current rating are connected in Series, it is completely normal for the "Larger" Size Device to Trip, either with or instead of the "Smaller" Branch Circuit Device.
The term "Non-Selective Coordination" is used to describe this event.
The reason behind this Non-Selective Coordination is simple:
The Upstream Device - most likely a 100A Multipole Device, is of the same Frame Type, Size and trip Characteristics, as the Smaller Branch Circuit Device; however, there is likely to be some Load being drawn by another Branch Circuit, prior to the Fault.
In this case, the Upstream Device reacts to the combined scenario as an Overload condition - which commonly results in only the Upstream Device being Tripped.
Example:
Frame Sizes = 125A, 120/240V, 10KAIC, Time-Trip Curve at 400A = .01 Seconds
100/3 Protecting Feeders supplying a 125A Panelboard, with multiple 20/1 Branch Circuit Devices installed.
Panelboard has the following Loads:
"A": 25 Amps
"B": 15 Amps
"C": 20 Amps
Ground Fault occurs on Branch Circuit #7 (Ph. A), approx. 50 Feet from the Panelboard - which results in an Instantaneous Fault Current level of 385 Amps.
Only the 100/3 Device Trips, as the Load at the Device is 410 Amps (385 + 25).
Back to the FPE devices!
FPE produced more Products, beside the "Stab-Lok" Line.
There are many FPE Devices in use today, in legacy Equipment, such as Zinsco, Westinghouse and GE Panelboards.
The Federal Pacific Transformer Company is still producing Transformers - Low Voltage Dry-Type, and Medium Voltage Oil-Immersed.
I prefer using FP Transformers, as they have the Terminals located more towards the Vertical Middle section of the Enclosure; makes Terminating large size Conductors much easier,
whereas most other Manufacturers place the Terminals at 8 to 12 Inches from the Bottom of the Enclosure; making it very difficult to Terminate large size Conductors.
Provided my 2¢
Leaving the Soapbox
--Scott (EE)
Almost forgot...
LOL! laugh
Scott35:
Thanks for the eloquent FPE info.
If memory serves me correct, the 1/2" 15-20 amp were the issues.
There are still many FPE fused discos around. I have not come accross any FPE transformers lately.
Well it's been 30+ years, but I grew up in a 24-unit apartment complex with FPE Stab-Loks throughout... My memories:
Apartment 24 - electric water heater shorted internally (line-ground). I was like 10 years old - neighbor (also young) came running to my house, parents not home, house is full of smoke, water heater is making scary noises. Breaker never tripped. I turned it off manually. Thank heavens that worked --- at that age, I don't think I would have had any clue what to do if it hadn't.
Apartment 5 - short in electric baseboard heater ended up tripping 100A main in meter stack (GE brand).
Apartment 2 - All units had one split-wired receptacle in the livingroom and each bedroom, the top half being wired to a wall switch. In some of the apartments, the top (switched) and bottom (unswitched) receptacles wound up on different circuits (MWBC). In apt 2, the maintenance man had replaced a damaged receptacle but did not remove the jumpers. When the switch was turned on, one of the breakers tripped, but only internally - it could not be reset.
Apartment 17 - during a conversion from electric heat/hw to centralized hydronic baseboard, heating contractor turned off breakers for electric baseboard dhw. DHW was still live despite breaker being "off," resulting during removal in light show and tripped main (again, GE)
Now, I will definitely say I am very much opposed to the FPE breakers installed in 24-unit apartment complexes in small Maine towns in 1980. Of course, some (or even most) of these failures could be blamed on age. During my time there, I proved multiple times (I was a curious/experimental youth...) that, most of the time, the breakers DID work...