There are no "county" rules in Florida and with a couple of exceptions the whole state is in the 2008 NEC unaltered by law. (the unified Florida building code
Greg Fretwell
|
|
|
|
Joined: Jun 2004
Posts: 613
Member
|
Thanks Greg. I thought I read that on a message board somewhere. So no ground rod required by the NEC unless it it set up as a SDS.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
It may be in the imagination of some inspector but if it is not in the NEC, it is not Florida law.
The only 2 amendments I can think of is one requiring bonding of steel studs and one a proposal for lifting the GFCI requirement on 240v hard wired pool pumps.
Greg Fretwell
|
|
|
|
Joined: Nov 2002
Posts: 244
Member
|
Just ran into this a couple weeks ago. 250.34 does not require a grounding electrode if the load is fed from receptacles mounted on the generator. How about if the load is cord is fed from the bolted lugs on the generator? Bolted lugs do not fit the definition of a receptacle so technically would a ground rod would be required?
|
|
|
|
Joined: Feb 2002
Posts: 2,233
OP
Member
|
At the generators are most of the neutrals tied to the grounding connection or are the separated in the generator?
|
|
|
|
Joined: Feb 2002
Posts: 2,233
OP
Member
|
Re-reading Soares book on grounding. If you are not breaking the neutral and you are using the homes grounding system, then the neutrals and grounds should be separate at the generator. Plus no ground rod.
|
|
|