1 members (Scott35), 552 guests, and 37 robots.
sidmuer Offline OP
Ok, if I have 100 AMP panel, in 60 degree ambient temperature, how would I size the wire??
Do I just do 100A x 1.25 for continuous = 125A then Table 5A says at 60 degrees using the middle column wire is .67
so then 125A / .67 = 186.5
So then I go back to table 2 using the middle column wire, I would choose 3 aught? (210AMP rated)
OR:
since 100AMP panel can use #3 rated for 105AMP. I just goto 105AMP / .67 for the 60 degree ambient temp and get: 156.7 = 2 aught (185AMP rated wire from middle column of Table 2 )
OR
is 100amp panels with #3 wire feeders only allowed for residential dwellings, and since it doesn't specify as a residential application/installation for this panel do I stick to the first method?
Thank you.
twh Offline
60 degree ambient is pretty warm. Do you mean 60 degree rating on the breaker?
sidmuer Offline OP
ambient...
it's a pen/paper test question.
twh Offline
I don't know that breakers are okay in a 60 degree ambient. Is it a trick? I'll give it some thought, anyway. Is it a 2012 code question?
twh Offline
26-402 says no panels in high ambient rooms. When do I get my marks?
Gentlemen:
Two (2) posts to this thread were deleted today. PMs were sent to the two gentlemen involved.
sidmuer Offline OP
based on 2009 CEC book.
hmm... table 5b (going off memory.. somewhere there... )
ambient adjustment factors to derate wires are listed there accordingly.
It's not for the panel, but for the wire. I guess where the wire run is happening, it can reach that temp.
sidmuer Offline OP
^^ nevermind that last response. I noticed my original question was regarding panels, not wire runs!!!
Thanks twh! smile
I got an interesting one for you. It is tricky.
I gotta look it up from my notes.
Here it is....
if I have 2500 WATTS heater and 240 VOLTS. I'd like to size the conductors.
do I go about it as such:
2500 / 120 = 20.833
So, here's the part that is tricky ( to me )
Do I need to pad that wire by x 1.25 for continuous load?
If so, I get 26AMP, and it's an easy #10 AWG answer from Table 2. However, if not, I'm left with 20.8A. That means, in T2 for conductor size, I would have to pick #10 since it is over 20. BUT..... SEC 8-106(1) states that if the next smaller size conductor has not more than 5% less than this minimum, the smaller size is permitted. Since 5% of 20 would be 1, and this falling at 20.8, does that mean I can use #12 ??
Or, am I totally misunderstanding 8-106(1) rule?
twh Offline
2500 watts and 240 volts = 10.4 amps
#14 and 15 amp circuit is fine even if you add the 1.25 factor which I am not sure about needing.