ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 506 guests, and 19 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Jan 2005
Posts: 91
H
Member
Can anyone please help me understand the purpose/meaning behind this article?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Looks to me that they are saying "no neutral in with the service, no neutral allowed inside the building." Guess they don't want you to count on the loads being perfectly balanced, or using the ground rod instead of a neutral.

Keep in mind that the NEC is attempting to address EVERY scenario. For example, the mill I'm at today is fed by the PoCo with three high-voltage 'hots.' There's no neutral from the PoCo. This means that we need a transformer to 'create' that neutral.

A lot of wells and pump houses are served by 'corner grounded' 3-phase power. If you want to have a neutral in that pump house, you'll need a transformer .... even if it's a "240 to 240" transformer.

After all, the electricity can't "go home" if the neutral wire doesn't go all the way back to the source.

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
This is what the handbook comment says.

Quote
Grounded conductors of premises wiring must be connected to the supply system (service or applicable separately derived system) grounded conductor to ensure a common, continuous, grounded system.


Greg Fretwell
Joined: Mar 2007
Posts: 101
M
Member
It is telling the installer that if you run a neutral ( grounded ) conducter you must terminate that conducter

Joined: Mar 2003
Posts: 849
Y
Member
See 250.24 C