Page 3 of 3 1 2 3
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I was going to bring that up myself wink

It can be ordered either way tho.


Greg Fretwell
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
The wiring on the load side of the service point has always had a full sized neutral in my experience.
I never gave much thought to what the PoCo was doing since I didn't have much ability to change it.


Greg Fretwell
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Greg:

Yes, triplex is reduced, but that is on their side!

My references are to typical NJ (PSE&G) secondaries that are 'customer installed' from pad mount xfrs. The rule also applies to O/H.



John
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I agree, everything on "my side" has had full sized neutrals.


Greg Fretwell
Joined: Oct 2000
Posts: 5,392
S
Member
God willing, and the creek don't rise (again!) I'll be installing 11 runs of 750KCMIL w/ 250 KCmil grounds monday

at first sniff that 250 seemed a tad small

but they're not calling it a neutral

they're calling it a groundING conductor (there's your 12.5%)

and 'earthing' a noodle from the 4000A 480 switchgear

this was engineered , and done so with both the poco and architectual engineers working in unision btw

all code ref's aside, i just don't like creating something that is readilly available, especially in close proximty to so many potential returns to the serving xfomer (or the other 2000A xfomer bank aboput 40' away)

~S~