#200697 04/14/11 11:54 PM
SJT Offline OP
A Service Main disconnect could be outside the building or in the Bldg. right?
If the main is outside (near a transformer)then the first panel it feeds in the Bldg. would be a sub panel?
SJT
SJT #200700 04/15/11 02:09 AM
Technically the service disconnect just has to be on the property but your AHJ may still want a disconnect on/in the building.
Yes that will become a feeder and you need to run the ECG along with a ground. As long as that is the feeder for the whole building, you can use 210.15(B)(6) in a dwelling. (Not commercial)
Last edited by gfretwell; 04/15/11 04:04 AM. Reason: Make the correction Niko pointed out
SJT #200701 04/15/11 03:36 AM
Greg meant, 310.15(B)(6) for 2008 and 310.15(B)(7) for 2011
SJT #200703 04/15/11 04:06 AM
Thanks. I guess I should turn up the light when I type
I am not on the 2011, in protest of the CD thing wink
SJT #200714 04/16/11 12:00 AM
Be cautious on the location 'within the building'. Unprotected, unfused, conductors within a building, the distance allowed is not specific in the NEC. For the most part, it's left up to the local AHJ. I hear 12", 5', 3'4", but there is NO distance within the book & never was.
A main inside is accepted 'nearest to the point of entry', unless we use the 2" of concrete/brick exception. It all boils down to the AHJ's 'nearest' definition
