#196793 10/27/10 04:37 PM
Joined: Oct 2010
Posts: 2
N
New Member
anyone hear that they are going back to using 75 degree column for ser/seu instead of 60 degree

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Feb 2003
Posts: 939
F
Member
Originally Posted by noshorts73
anyone hear that they are going back to using 75 degree column for ser/seu instead of 60 degree


AFAIK not yet until someone do get the 2011 NEC code book with the infomation on SER/SEU cable so hold on until someone will get that infomation and post it for ya.

Merci,
Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
From 2011 NEC Article 338.10 (B) 3 & 4:

"(3) Temperature Limitations. Type SE service-entrance
cable used to supply appliances shall not be subject to conductor
temperatures in excess of the temperature specified
for the type of insulation involved.
(4) Installation Methods for Branch Circuits and Feeders.
(a) Interior Installations. In addition to the provisions
of this article, Type SE service-entrance cable used for interior
wiring shall comply with the installation requirements
of Part II of Article 334, excluding 334.80.
Where installed in thermal insulation, the ampacity shall
be in accordance with the 60°C (140°F) conductor temperature
rating. The maximum conductor temperature rating
shall be permitted to be used for ampacity adjustment and
correction purposes, if the final derated ampacity does not
exceed that for a 60°C (140°F) rated conductor.
Informational Note No. 1: See 310.15(A)(3) for temperature
limitation of conductors.
Informational Note No. 2: For the installation of main
power feeder conductors in dwelling units refer to
310.15(B)(7).
(b) Exterior Installations. In addition to the provisions
of this article, service-entrance cable used for feeders or
branch circuits, where installed as exterior wiring, shall be
installed in accordance with Part I of Article 225. The cable
shall be supported in accordance with 334.30. Type USE
cable installed as underground feeder and branch circuit
cable shall comply with Part II of Article 340.