545
21
Posts: 9,931 Likes: 34
Where this seems most troubling is in town houses or duplexes, running through the attic. I have never seen it but the example presented was meter mains on one end of the building feeding the units via the attic using a cable. I don't remember where the thread was but if I get a few minutes I will see if it is still up.
I was working in a relatively new condo complex a while back and in the basement of the first unit behind the meter stack, I noticed all the SER’s for the other individual units running right through the floor joists above, so apparently there’s no code issue with that here either. With commercial, I think almost all would be in conduit around here anyway, so power theft might be at least a little more difficult. I suppose all they would need to do is cover the conduits with 2” of concrete and it would be considered outside the building.
That was kind of the thrust of the conversation. The feeder would be an attractive target for a power thief and the danger presented by the flying tap is sizable. The best you could hope for would be a Kupltap and worst case would be a hose clamp and duct tape.
Greg,
I have seen a lot of those feeders running through attics in the condos around here. Like everyone else is saying, not fond of it, but can't fail it.
Posts: 7,382 Likes: 7
Harold: The condo developement that is on the last bldg (22 units each) has each units feeder run thru the common hallways, and the risers are thru a common chase to the second & third floors.
The feeders thru the common hallways are installed within the truss type floor joists, fire/draft stopped at all penetrations, and then one layer of 5/8 FC shtrk is installed on the bottoms of the joists. Framing is then installed (8" drop) and the sprinkler lines, HVAC and any other items are mounted in this space, and the bottom is rocked w/ 5/8". The common chase mentioned above is 5/8 rock inside & out.
There are no feeders in the truss attics, only required lighting & radon fans.
Now, the 'old' buildings.....that's another story....
