ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 565 guests, and 35 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#194635 06/14/10 03:44 PM
Joined: Jun 2007
Posts: 106
M
Member
Correct me if I am wrong but since NMWU has a 60 degree rating, then #6NMWU is only good for 55Amps unless it is part of a residential service? (T.2 of the OESC) I am guessing that a sub panel to the garage would not fall under this classification therefore limiting my amperage rating to 55amps and not 60?


Never trust an electrician with no eyebrows!!
Joined: Jun 2006
Posts: 613
M
Member
I think that as long as the Garage is a residential garage and part of a single residential unit, then 60 amps would apply. A residential Garage is not a continuous load and residential services are non continuous loads.
A duplex with a single joint use garage might not qualify.

Talk to the local authority but I think we would allow the greater ampacity as long as the Volt drop does not get rediculous.

Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Isn't it a 55 amp feeder fused at 60 amps per Table 13? The differences are that if the load in the garage is greater than 55 amps, the wire is too small; and, the location of the panel in the garage isn't restricted like a residential service.

Joined: Oct 2010
Posts: 9
S
New Member
good luck finding a 55 amp breaker

Joined: Jun 2006
Posts: 613
M
Member
Twh
Yes you make the most important point. As long as the calculated load is less than 55 amps then the #6 is good and table 13 would allow a 60 amp breaker.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5