421
27
Is there room to install three 40 A solid link disconnects in the laundry room? Could they all be tied together with a piece of all thread so they all operate together?
Posts: 9,931 Likes: 34
"All thread" is not a "listed handle tie" so that would be a no.
I wonder if 6 pole pull-outs similar to the the cheapie air conditioner disconnects are available. If not, it seems it's a ripe time to market something like that.
Economically, does it make sense to use a mechanically held lighting contactor? The idea being that a simple toggle switch would throw six poles.
I remember 20A and 30A rating contactors by SqD.
Is any NEMA player coming out with a sweet solution for this application?
Tesla
You can't use contactors as disconnects.
Posts: 7,382 Likes: 7
Guess a sub-panel with a 'main' and three branch CBs is a way to go.
The lock-out (if needed by placement) could be installed on the 'main'. (Two pole like may be used on an oven/range)
Oddly, I only came accross one job with this type unit about 2 years ago, the Ec was debating how to do this when I was there for a rough, and that job is still at a standstill ($$$$) Strange thing was the house has a 150 amp service!
I would be interested in the load calc that would allow a 110 a water heater on a 150a service. What kind of range and HVAC equipment do they have?
Greg: This is a resi that has an addition, with a service upgrade to 400 amp. The job has been at a standstill for quite some time (1 1/2 to 2 years) due to $$$$. The EC at the time was basically a lost soul with a few items, the WHtr only one of them.
Greg,
I agree that a sub panel by the water heater would be the best option. However what if there is no room? Say the new water heater is in a closet with no room for a sub panel? Then what?
That is the same problem we have with air handlers. The AHJ has to make up his mind, do we waive 110.26 or the "within sight" rule. I guess that is why we make the big bucks
CDS
Nicholson Ga