Y
MCA 74 on compressor unit (all mts taken into account).
240 v single phase to 240 v 3 phase.
40 hp convertor .
input Aprox 127 amps
outputaprox 100 amps.
Comments???
Yoopersup
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
twh Offline
I'm guessing you're looking at a rotary converter. Do the motors need to be de-rated? The math looks off between single phase input and 3 phase output.
Tom Offline
Any chance of doing this with VFD's? Appropriately sized VFD's can convert a single phase input to three phase.
Few things are harder to put up with than the annoyance of a good example.
Y
This is a Full HVAC unit was ordered wrong. MCA on name plate 74 amps single point hookup.
So need about 80 amps or so on three phase side.
As starteres ect are all ready in the package looking for 3 phase power imput. Vendor told us 40 hp unit well do the trick just checking.