|
1 members (Scott35),
565
guests, and
35
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2004
Posts: 947
OP
Member
|
What type of switch is best for an appliance garage? Is there a limit switch that has a 20 amp rating?
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
|
|
|
|
Joined: Mar 2004
Posts: 947
OP
Member
|
To switch the receptacle.
An appliance garage is a box with doors on a kitchen counter where people put things like toasters and food processors. The receptacle has to be off if the door isn't open.
|
|
|
|
Joined: Nov 2005
Posts: 827 Likes: 1
Member
|
I would want the limit switch to control a contactor in an application like that. I would be inclined to have a thermal switch in series with it too. Joe
|
|
|
|
Joined: Aug 2006
Posts: 356
Member
|
why does the receptacles have to be OFF? my first time hearing this.
Be kind to your neighbor, he knows where you live
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
I think I know what you are refering to this and just a suggest but a door jamb switch may work for your useage but the curpit is the rating of jamb switch IIRC it will be about either 5 or 12 amps depending on what model you get.
Merci,Marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Aug 2002
Posts: 402
Member
|
The OP is in Canada. It is code up here for the receptacle be off if the door is shut.
|
|
|
|
Joined: Dec 2002
Posts: 337
Member
|
Square D has a class 9006 L100/300 series rated for 20 amp continuous (page 21-34, digest 175) but you are going to pay for it. Other manufacturers have similar but I don't have current catalogues. As far as size goes I would go for the small switch (less damage to the cabinet over time) to a relay, it may be about similar in bulk. I am glad we don't have that requirement.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
I'm going to move this to the Canadian Code Section.....may get the appropriate responses there.
John
|
|
|
|
Joined: Mar 2004
Posts: 947
OP
Member
|
Square D has a class 9006 L100/300 series rated for 20 amp continuous I thought it was a normal thing for residential work, but the wholesalers haven't heard of such a thing, and I have to do two. At the first I used a limit switch and a 20 amp relay, because the wholesalers told me a 20 amp limit switch isn't available. Now I know better and I think the switch alone is a better option. Thanks sabrown.
|
|
|
Posts: 404
Joined: March 2007
|
|
|
|
|