The Electrical Contractor Network
ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals
Books, Tools and Test Equipment for Electrical and Construction Trades
Live Chat
Join in a Live Electrical Chat!
>> Enter/Register
  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
4" PVC Conduit For Sale - Chicago
by acastillo
44 minutes 12 seconds ago
4" PVC Conduit For Sale In Chicago
by acastillo
44 minutes 54 seconds ago
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Today at 09:25 AM
450.3(C)
by gfretwell
Yesterday at 09:32 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
An old Amprobe model 550
Shout Box
Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:
Electrical-Classifieds.com
Who's Online
4 registered (jdevlin, sidmuer, twh, ampherder), 129 Guests and 3 Spiders online.
Topic Options
Rate This Topic
#192333 - 02/08/10 03:42 PM Old work grounding stumper
Haligan Offline
Loc: Berkeley, CA USA
The Scene:
Old work bathroom remodel. GC has it down to the studs.
I'm keeping the existing circuit for lights and fan. 12/2 NM, no grounding
I've pulled a homerun 20a for receps.
How to ground the lights and fan?
A. There's a bare 14ga conductor that was bonding all of the old metal boxes. It is clamped with a grounding electrode to the bathroom's water pipe. This wire then continues off to other parts of the house. I could tap into this. But! Code says bonding to water pipe has to be 5' from source. This seems like a 'better than nothing' option. My least favorite so far.
B. Connect to the grounding of the new 20a circuit. This goes back to the panel and straight to the rod. Problem- I scoured the code and couldn't find an allowance for this.
C. Connect a new electrode and ground the lights and fan to the water pipe.
D. Run 12ga grounding wire all the way back to the panel. This is okay code wise, but raises some new issues.
What's best here?
Top
#192334 - 02/08/10 05:52 PM Re: Old work grounding stumper [Re: Haligan]
Jim M Offline
Loc: Chestertown, MD, USA
Since you are down to the studs I would think that a new lighting circuit should be run.
Top
#192336 - 02/08/10 06:26 PM Re: Old work grounding stumper [Re: Jim M]
HotLine1 Offline
Loc: Brick, NJ USA
I tend to agree with Jim M.
You may want to run your list of options past the local AHJ, as he is the one to accept or reject your choice(s).
_________________________
Top
#192337 - 02/08/10 07:51 PM Re: Old work grounding stumper [Re: HotLine1]
gfretwell Offline
Loc: Estero,Fl,usa
Best practice would be to run a new wire. Your ideas of using the water pipe, even with another rod, won't work unless you bond back to the existing ground electrode system.
You could share the EGC of the new receptacle circuit you have run but you do have to worry about protecting the wire you run. I would ask if your AHJ is OK with just stringing a THHN over to the receptacle box
Quote:
250.120(C) Equipment Grounding Conductors Smaller Than 6 AWG. Equipment grounding conductors smaller than 6 AWG shall be protected from physical damage by a raceway or cable armor except where run in hollow spaces of walls or partitions, where not subject to physical damage, or where protected from physical damage.
Top
#192338 - 02/08/10 08:58 PM Re: Old work grounding stumper [Re: gfretwell]
George Little Offline
Loc: Michigan USA
Guess I'm trying to figure out why anything has to be done with existing. But if you insist on doing something, item D. is the only one that meets code.
George Little
Top
#192339 - 02/08/10 09:34 PM Re: Old work grounding stumper [Re: George Little]
gfretwell Offline
Loc: Estero,Fl,usa
I was just trying to let safety trump a technical violation (extending the EGC from an existing circuit of sufficient size). I would rather have a ground than not.
Top
#192340 - 02/08/10 10:38 PM Re: Old work grounding stumper [Re: gfretwell]
Loc: Michigan USA
I guess I agree with you Greg and I would add, another option would be to wire the fan and lights in the bathroom on the new receptacle circuit. As long as he didn't extend to anything beyond the one bathroom, he'd have not only grounding but GFCI protection ta boot.
George Little
Top
#192341 - 02/08/10 11:36 PM Re: Old work grounding stumper [Re: George Little]
Haligan Offline
George- I'm liking 210.11(C)3. The lights and the fan sum up to less than 1amp. Plenty of leftover on the 20a dedicated.
Thanks all
Top
#192345 - 02/09/10 08:29 AM Re: Old work grounding stumper [Re: George Little]
Rewire Offline
Loc: Missouri
The only method that would be questionable would be B but all the others are code compliant
Top