1 members (Scott35),
57
guests, and
11
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Feb 2004
Posts: 115
OP
Member
|
Both are permissible, so how to decide?
With the breaker it's more of a hassle to run to the panel to reset, especially if it's at a distance, even more so if you're wet and naked. But I can't remember the last time I've seen a GFCI trip.
opinions anyone?
|
|
|
|
Joined: Apr 2002
Posts: 7,383 Likes: 7
Member
|
IMHO, it's a design issue, as both are NEC compliant. Also, it's a convenience thing, as you said regarding running and wet.
As to tripping, the one for my laundry circuit tripped a few weeks back...reason unknown. As an inspector, I 'trip' quite a few each day (hopefully).
A personal opinion of mine is a few McMansions that have a GFI in the powder room (first floor) that runs thru to a few other baths. But, that's a design issue!
John
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
The problem that I see with chaining GFI receptacles in several bathrooms is that inevitably someone will be using the bathroom that the reset button is in while I'm wet and naked in the corridor banging on the door because the bathroom that I was in is downstream of it.
"Murphy was an optimist"
Ghost307
|
|
|
|
Joined: Feb 2008
Posts: 165
Member
|
A GFI receptacle is alot less cost than a GFI breaker.Although legal by code I would never recommend daisy chaining bath recepts.The last custom we did actually had two circuits for the master bath receptacles.
|
|
|
|
Joined: Feb 2004
Posts: 115
OP
Member
|
It's a tiny bathroom. 1 sink. I'm only putting 2 receps for convenience. They'll be the only things on the dedicated 20a, and I'm wiring them in parallel.
The 20a gfci breaker is already in the panel from somebody before me.
I've made it clear the penalty for dropping the hairdryer in the toilet is having to run up a flight of stairs into the garage to reset the GFCI. not to mention buying a new hairdryer plus a little .5 amp zinger.
or is it .05. Or is that DUI?
|
|
|
|
Joined: Feb 2008
Posts: 165
Member
|
It's a tiny bathroom. 1 sink. I'm only putting 2 receps for convenience. They'll be the only things on the dedicated 20a, and I'm wiring them in parallel.
The 20a gfci breaker is already in the panel from somebody before me.
I've made it clear the penalty for dropping the hairdryer in the toilet is having to run up a flight of stairs into the garage to reset the GFCI. not to mention buying a new hairdryer plus a little .5 amp zinger.
or is it .05. Or is that DUI? The funny thing is dropping the hairdryer in the toilet wont trip the GFI.
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
... I've made it clear the penalty for dropping the hairdryer in the toilet is having to run up a flight of stairs into the garage to reset the GFCI. ... I would not expect it to trip the GFCI as I have never seen a hair dryer with a 3 wire cord. In the absence of an EGC in the hair dryer cord, there is no current path other than hot to neutral when you drop it into the toilet.
Don(resqcapt19)
|
|
|
|
Joined: Jul 2004
Posts: 9,935 Likes: 34
Member
|
It should still trip the immersion detector in the plug. There is a 3 wire cord in a hair dryer but the 3d wire just connects to a ring in the barrel of the dryer. It is similar to a GFCI but it is looking for any current in that 3d wire from either line side conductor.
Greg Fretwell
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
It should still trip the immersion detector in the plug. There is a 3 wire cord in a hair dryer but the 3d wire just connects to a ring in the barrel of the dryer. It is similar to a GFCI but it is looking for any current in that 3d wire from either line side conductor. Yes, that is the purpose of the immersion detector, I was talking about the branch circuit GFCI protection. It is very unlikely that a two wire device will trip the branch circuit GFCI when the device is dropped in a toilet....unless the toilet is an all metal one like found in prisions.
Don(resqcapt19)
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
as an aside here, if one does opt for a panel GFI breaker, and daisychain all the non-dedicated gfci required receptacles back to it, doesn't the length of said circuit's R factor start to influence that 5ma?
~S~
|
|
|
Posts: 524
Joined: December 2003
|
|
|
|
|