Electricians revenge
0 members (), 205 guests, and 12 robots.
Y
600 volt three conductor (310.20??), or 4160 three conductor(310.73??) either with messager.
Yoopersup
If the 3 conductors are in a metal jacket I don't think any "free air" table applies (one opinion).
IMO: Not only do you use the 'standard' table (310.16), but you might even have to derate for heat (in the sun), as you wpould were they over a rooftop.
I believe the 2008 also would require this MC to be in a waterproof jacket as well.
Y
310.73 MV : In Isolated CONDUIT in air. So that one I;m pretty sure of.
310.18 LV : Not sure of?
K
For the 600V, I think you may need to use Table B.310.3 in Annex B, since it specifically mentions type MC cable in free air.
For over 2000V though, with three conductors, I believe you could use table 310.71, since IMO, the MC jacket is not actually a conduit or raceway as defined in Art.100.
K
I probably should have said you may want to use Table B.310.3 in Annex B.
Just carious, why are you stringing MC on a messager? Or am just interpting something wrong here?
Y
MC cable on Industrial sites is quite often put on poles to remote pumping stations ect. Both 600v & i;ve even see 15kv in MC on poles.
Yoopersup
I have never seen it before either, which tends to explain my silly answer above, sorry for the confusion. wink
Y
mc cable 330.10 (B)4.
Installed outside of buildings or structures or as aerial cable.
type mc cable installed outside of buildings or structures or as aerial cable shall comply with 225.10,396.10,& 396.12.
