For the 600V, I think you may need to use Table B.310.3 in Annex B, since it specifically mentions type MC cable in free air.
For over 2000V though, with three conductors, I believe you could use table 310.71, since IMO, the MC jacket is not actually a conduit or raceway as defined in Art.100.