Maybe it's just the lighting (or lack thereof), but that portion of the liquidtight hanging out in the breeze (in the foregroud of the pic.) doesn't look very healthy either. Certainly a poor substitute for a nice pipe job.
This isn't a hazardous area, is it?
Mike (mamills)
|
|
|
|
Joined: Mar 2009
Posts: 73
OP
Member
|
Maybe it's just the lighting (or lack thereof), but that portion of the liquidtight hanging out in the breeze (in the foregroud of the pic.) doesn't look very healthy either. Certainly a poor substitute for a nice pipe job.
This isn't a hazardous area, is it?
Mike (mamills) The liquidtight dangling down in the dim conditions is under a metal staircase coming from the second floor of the building down to the ground. It isn't accessible, and seems isolated enough to be safe from physical damage. I don't know if it classifies as a 'hazardous area" by definition, though. A wider angle view.
Last edited by Bigplanz; 05/19/09 04:48 PM.
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
I have heard arguments that those connectors are only listed for boxes and cabinet K/Os. They say using them with a threaded connector is a violation.
Greg Fretwell
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Over here in NJ we calll the 'Mineralacs' "cowboys"! BTW, are they listed for sealtite?
The wide angle view now reveals .....unsupported EMT; is the disco holding the EMT? or...is the EMT holding the disco?
John
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
I assume you are referring to the transition where a threaded coupling was used to transition from Sealtite to pipe.
I even have seen a statement by UL in print that claimed that such use of the threaded coupling was improper .... but it was hard to be sure. UL has engineers, not writers, and their prose is often poor. (Just look at any of their standards!)
It's certainly a matter of lively debate in some circles. Alas, the most strident voices of opposition seem unable to back their opinion with more than their egos.
Personally, I don't have an issue with it at all .. and certainly not when there's a ground wire in the run.
As for the argument that "you can't make a piece from parts that is factory made," I have nothing but contempt. Indeed, the 'factory' stuff is usually inspired by the successful use of a field-made assembly.
|
|
|
|
Joined: Mar 2009
Posts: 73
OP
Member
|
Over here in NJ we calll the 'Mineralacs' "cowboys"! BTW, are they listed for sealtite?
The wide angle view now reveals .....unsupported EMT; is the disco holding the EMT? or...is the EMT holding the disco? If you take a close look at the bottom left hand corner, you can see the EMT is supported by a big block of wood. Here is a blow up.
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
Violation: 350.30(A) (supported with in 12" 0f a box)
Very ugly Yes. This may be compliant under 'Exception 2' of 350.30 (A) No way. it is on a disco,besides,How are you going to move that conduit?
|
|
|
|
Joined: May 2005
Posts: 984 Likes: 1
Member
|
I must have misunderstood the scale; it looked like the block of wood is more than 12" from the disconnect switch. That switch must be only 2" or so in height.
BTW, is that REALLY "supporting" the conduit or just propping it up so it doesn't rip out of the bottom of the enclosure by its own weight??
Ghost307
|
|
|
|
Joined: Mar 2009
Posts: 73
OP
Member
|
I must have misunderstood the scale; it looked like the block of wood is more than 12" from the disconnect switch. That switch must be only 2" or so in height.
BTW, is that REALLY "supporting" the conduit or just propping it up so it doesn't rip out of the bottom of the enclosure by its own weight?? Tbe block of wood is more than 12" from the disconnect. I would say it's close to three feet below the disco. As far as the question of 'support' that's a good one. Is the conduit properly 'supported' or not, by code? I don't know. The weight of the conduit is borne by the wood, so I would say, 'yes, it is supported.' Whether it is supported in a code compliant way is a different matter.
|
|
|
|
Joined: Mar 2009
Posts: 73
OP
Member
|
At the same site, I came across this oddity. Not sure what to make of the flex just cut off and left dangling from the disco. Hope it's not hot, anyway. As my teenage daughter would say, WTF?!?
|
|
|
Posts: 57