ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 504 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Mar 2006
Posts: 82
B
bigpapa Offline OP
Member
Is this conductor derating because of higher temperatures in the transformer?

Joined: Jun 2007
Posts: 106
M
Member
Originally Posted by bigpapa
Is this conductor derating because of higher temperatures in the transformer?

No, the 125% is to accomidate the inrush current that happens when a transformer is energized.


Never trust an electrician with no eyebrows!!
Joined: Sep 2006
Posts: 111
E
Member
Originally Posted by mr_electrician
Originally Posted by bigpapa
Is this conductor derating because of higher temperatures in the transformer?

No, the 125% is to accomidate the inrush current that happens when a transformer is energized.


Inrush from a transformer? I assumed only motors have an inrush current when energized. I'm going to test that tonite. I have to shut down some power after hours.


Joined: Jul 2005
Posts: 183
J
Member
AC squirrel cage induction motor and transformer are essentially the same, with the motor having the secondary (or rotor) shorted out. I dont think you will see large inrush on a transformer as in a motor unless the transformer is loaded up to its rated KVA.

Joined: Jul 2004
Posts: 787
L
Member
I will disagree on that statement. I have heard the conductors SLAP in the conduit when energizing an unloaded transformer. I believe it is called magnetizing current.

In essence, the inductive reactance of the transformer is zero until the current starts flowing, therefore the transformer looks like a short circuit upon energization. A large current starts to flow, which produces strong magnetic fields, which pushes the conductors away from each other, resulting in the slapping of the conductors against the conduit.

Larry C

Joined: Aug 2007
Posts: 853
L
Member
Ive heard that with elevators and other large motors before.

Joined: Jun 2007
Posts: 106
M
Member
Originally Posted by LarryC
I will disagree on that statement. I have heard the conductors SLAP in the conduit when energizing an unloaded transformer. I believe it is called magnetizing current.

In essence, the inductive reactance of the transformer is zero until the current starts flowing, therefore the transformer looks like a short circuit upon energization. A large current starts to flow, which produces strong magnetic fields, which pushes the conductors away from each other, resulting in the slapping of the conductors against the conduit.

Larry C

And that is why we size the conductors 125%. Because of the inrush, not ambient temperature.


Never trust an electrician with no eyebrows!!
Joined: Mar 2004
Posts: 947
T
twh Offline
Member
Rule 26-256 puts the overcurrent at 125%, so the conductor at 125% matches the overcurrent.

Joined: Mar 2006
Posts: 82
B
bigpapa Offline OP
Member
26-258 (3) contradicts any inrush theory. We are allowed to use a 75 kva transformer for example where you would need 60 kva and size the conductors as if you had a 60 kva transformer. Seems that inrush is not considered as long as the overcurrent device does not operate. Not a good design practice sometimes.
Stating that conductors are required to be sized at 125% because it says so in 26-256 is not really answering the question of what exactly are we derating for. I'm sure there is a reason somewhere.

Joined: Jun 2006
Posts: 613
M
Member
It is all to do with ampacity of the load. Transformers are continuous loads and conductors are sized per all other continuous loads. Our electrical equipment is sized this way. It deals with the heating from the conductor on the breaker and the transformer terminals. Conductors are sized to the rating of the transformer and not the O/C device.
You size the conductors for a hot water heater or a lighting load the same way. It sometimes appears a little differently when we say you can only load a 15 amp breaker to 80% but we could think that is the inverse of 125%. In the case of a plug circuit we wire with #14 and the 15 amp wire is only loaded to 80% or 12 amps.
I hope I am making sense.
A 75 KVA transformer is 208 amps at 208 volts the wire must be 260 amps. (75000/208*1.73)1.25 The other way to look at it is what is the largest load than can be connected to 260 amp wire? 260*.8 or 208 amps @ 208 volts 3 phase(75 KVA)


Link Copied to Clipboard