The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured Items:

Switch Bit - Interchangeable Flex Bit System
>> Switch Bit -
Interchangeable Flex Bit System

>> 2014 NEC and Related

Recent Posts
RFI/EMI RF Filter
by LarryC
12/22/14 06:28 PM
Old Devices and Cover Plates
by gfretwell
12/22/14 11:42 AM
Single Pole Control Switch On 240-v Motor
by gfretwell
12/22/14 11:38 AM
Possible to install Schuko outlet in US?
by chrisBTPA
12/21/14 03:35 PM
Euro outlet in US kitchen
by Meadow
12/20/14 09:55 PM
New in the Gallery:
Another find....
Shout Box

Top Posters (30 Days)
gfretwell 23
Meadow 18
dsk 16
renosteinke 15
HotLine1 15
Who's Online
1 registered (LarryC), 69 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#184917 - 02/25/09 03:03 PM flexible cord thru drop ceiling?
CRW Offline
Member

Registered: 02/11/01
Posts: 160
Loc: Bethlehem, PA USA
Are there any scenarios where you can run a flexible cord through a drop ceiling? I was told we could run a cord from a box above a ceiling, through the tile, with a cord connector on the end. This is for an appliance that is in the middle of an institutional kitchen, away from the wall, so we can't use a fixed receptacle. 400.8(2) seems to not permit this, but it also says, "Unless specifically permitted in 400.7..." which could then refer to 400.7(6)&(8). I questioned this whole thing at work (without citing the actual code, I didn't have it with me at the time) but the foreman said it was OK to do. What do you think?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#184919 - 02/25/09 03:29 PM Re: flexible cord thru drop ceiling? [Re: CRW]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
400.7 says nothing of passing through ceilings. it speaks to cords for equipment.
400.8 is the guide.

I would install a ceiling box and drop a cord with strain relief and twist lock cap.Don't forget,if it is 120 volt 15 or 20A GFCI is needed. 210.8(B)(2)


Edited by leland (02/25/09 03:30 PM)
Edit Reason: 210.8

Top
#184921 - 02/25/09 04:56 PM Re: flexible cord thru drop ceiling? [Re: leland]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5060
Loc: Blue Collar Country
Passing a cord through the ceiling tile, as you describe, is a code violation in two ways: there's a flexible cord above the grid, and the cord is passing through a partition.

That said ... I recognize that this is often done, and that circumstances often make even a ceiling box impractical. I'm not quite sure where to go with this ... maybe a proposal for the next NEC cycle - but I'm not sure how one would write it.

Drop ceilings, once the 'wunderkind' of building, are quickly becoming a major headache. Perhaps their time has passed.

Top
#184927 - 02/25/09 05:49 PM Re: flexible cord thru drop ceiling? [Re: renosteinke]
HotLine1 Online   content

Member

Registered: 04/03/02
Posts: 6326
Loc: Brick, NJ USA
Another old addage from NJ....

"Drop ceilings hide a multitude of sins"

That said, cord thru the tile is a no-no. A ceiling grid mounted box, suitable coverm strain relief, & TL is accepted

However, a TL recept mounted in the ceiling box, face down, that the cord from the equip plugs into may be a better way.

Some AHJ's cite the cord from the ceiling box in the first scenario as using cord for permanent wiring, and red flag this, absed on 400.7 & 400.8 interpertations.
_________________________
John

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals