The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


Recent Posts
Old British switches
by LongRunner
Today at 12:47 PM
When would you choose Al over Cu for an install?
by Texas_Ranger
11/24/15 05:20 AM
A Letter to the IAEI
11/24/15 02:45 AM
FPE Revisited
by HotLine1
11/22/15 12:35 PM
Swiss code violations
by Texas_Ranger
11/22/15 11:35 AM
New in the Gallery:
Access ??
Shout Box

Top Posters (30 Days)
gfretwell 25
HotLine1 19
renosteinke 15
Texas_Ranger 10
annemarie1 8
Who's Online
0 registered (), 105 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#184917 - 02/25/09 03:03 PM flexible cord thru drop ceiling?
CRW Offline

Registered: 02/11/01
Posts: 160
Loc: Bethlehem, PA USA
Are there any scenarios where you can run a flexible cord through a drop ceiling? I was told we could run a cord from a box above a ceiling, through the tile, with a cord connector on the end. This is for an appliance that is in the middle of an institutional kitchen, away from the wall, so we can't use a fixed receptacle. 400.8(2) seems to not permit this, but it also says, "Unless specifically permitted in 400.7..." which could then refer to 400.7(6)&(8). I questioned this whole thing at work (without citing the actual code, I didn't have it with me at the time) but the foreman said it was OK to do. What do you think?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#184919 - 02/25/09 03:29 PM Re: flexible cord thru drop ceiling? [Re: CRW]
leland Offline

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
400.7 says nothing of passing through ceilings. it speaks to cords for equipment.
400.8 is the guide.

I would install a ceiling box and drop a cord with strain relief and twist lock cap.Don't forget,if it is 120 volt 15 or 20A GFCI is needed. 210.8(B)(2)

Edited by leland (02/25/09 03:30 PM)
Edit Reason: 210.8

#184921 - 02/25/09 04:56 PM Re: flexible cord thru drop ceiling? [Re: leland]
renosteinke Offline
Cat Servant

Registered: 01/22/05
Posts: 5193
Loc: Blue Collar Country
Passing a cord through the ceiling tile, as you describe, is a code violation in two ways: there's a flexible cord above the grid, and the cord is passing through a partition.

That said ... I recognize that this is often done, and that circumstances often make even a ceiling box impractical. I'm not quite sure where to go with this ... maybe a proposal for the next NEC cycle - but I'm not sure how one would write it.

Drop ceilings, once the 'wunderkind' of building, are quickly becoming a major headache. Perhaps their time has passed.

#184927 - 02/25/09 05:49 PM Re: flexible cord thru drop ceiling? [Re: renosteinke]
HotLine1 Offline


Registered: 04/03/02
Posts: 6602
Loc: Brick, NJ USA
Another old addage from NJ....

"Drop ceilings hide a multitude of sins"

That said, cord thru the tile is a no-no. A ceiling grid mounted box, suitable coverm strain relief, & TL is accepted

However, a TL recept mounted in the ceiling box, face down, that the cord from the equip plugs into may be a better way.

Some AHJ's cite the cord from the ceiling box in the first scenario as using cord for permanent wiring, and red flag this, absed on 400.7 & 400.8 interpertations.