Joined: Feb 2001
Posts: 159
OP
Member
|
Are there any scenarios where you can run a flexible cord through a drop ceiling? I was told we could run a cord from a box above a ceiling, through the tile, with a cord connector on the end. This is for an appliance that is in the middle of an institutional kitchen, away from the wall, so we can't use a fixed receptacle. 400.8(2) seems to not permit this, but it also says, "Unless specifically permitted in 400.7..." which could then refer to 400.7(6)&(8). I questioned this whole thing at work (without citing the actual code, I didn't have it with me at the time) but the foreman said it was OK to do. What do you think?
|
|
|
|
Joined: Aug 2007
Posts: 853
Member
|
400.7 says nothing of passing through ceilings. it speaks to cords for equipment. 400.8 is the guide.
I would install a ceiling box and drop a cord with strain relief and twist lock cap.Don't forget,if it is 120 volt 15 or 20A GFCI is needed. 210.8(B)(2)
Last edited by leland; 02/25/09 07:30 PM. Reason: 210.8
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Passing a cord through the ceiling tile, as you describe, is a code violation in two ways: there's a flexible cord above the grid, and the cord is passing through a partition.
That said ... I recognize that this is often done, and that circumstances often make even a ceiling box impractical. I'm not quite sure where to go with this ... maybe a proposal for the next NEC cycle - but I'm not sure how one would write it.
Drop ceilings, once the 'wunderkind' of building, are quickly becoming a major headache. Perhaps their time has passed.
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Another old addage from NJ....
"Drop ceilings hide a multitude of sins"
That said, cord thru the tile is a no-no. A ceiling grid mounted box, suitable coverm strain relief, & TL is accepted
However, a TL recept mounted in the ceiling box, face down, that the cord from the equip plugs into may be a better way.
Some AHJ's cite the cord from the ceiling box in the first scenario as using cord for permanent wiring, and red flag this, absed on 400.7 & 400.8 interpertations.
John
|
|
|
Posts: 44
Joined: August 2005
|
|
|
|