The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
100AMP panel in 60 degree ambient what size wire?
by mikesh
Today at 06:49 PM
450.3(C)
by Steve T
Today at 05:41 PM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
Yesterday at 11:37 PM
Housekeeping and Clean-up
by renosteinke
Yesterday at 12:52 PM
Back to back bends on electric bender
by Tesla
05/20/12 05:38 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
HotLine1 27
gfretwell 27
sparkyinak 17
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 124 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#184379 - 02/08/09 09:49 PM Question About Recessed Lights
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
Posted for George Little:


Quote:
I have a question that may not be relevant in all States but here in Michigan they just adopted a version of the energy code that affects recessed lights in the insulation envelope of a residence. Is it equivalent to use an air tight recessed can with a open trim and/or a IC can and a trim that has the letters "AT" in the model number. I have had no experience with either.
_________________________
George Little

Top
#184380 - 02/08/09 11:09 PM Re: Question About Recessed Lights [Re: electure]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
In Massachusetts,Yes. The 'AT' Is an enclosed fixture housing.
These must be used on the upper floors (attic) and between tenants (over under).

Top
#184383 - 02/09/09 12:09 AM Re: Question About Recessed Lights [Re: leland]
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 932
Loc: Wi/ Paris France { France for ...
I do know in State of Wisconsin do required AT { air tight } for any area where it will be in concat with insulating materals { it don't matter if batt or blow in type }
And in France they just adopted not too long ago as well for recessed cans I do belive they have few additonal code requirement as well.

Merci,Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#184390 - 02/09/09 08:13 AM Re: Question About Recessed Lights [Re: frenchelectrican]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
Air tight cans with matching (AT) listed trims.
_________________________
John

Top
#184391 - 02/09/09 10:13 AM Re: Question About Recessed Lights [Re: HotLine1]
George Little Offline
Member

Registered: 01/18/04
Posts: 1445
Loc: Michigan USA
The issue that I am asking about has to do with the contractors using IC cans and then using AT trims. The claim is that the trim gives them the required energy code requirements. I have to believe that the trims used on the cans need to be Listed for use with that can and vise versa. I think the installer should be using AT cans in the insulation envelope to comply with the energy code and the can should be finished off with an AT trim.
_________________________
George Little

Top
#184392 - 02/09/09 10:32 AM Re: Question About Recessed Lights [Re: George Little]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
The way I understand it (I'll research more),One or the other or both will meet the standard.

Not an Inspector.

Top
#184413 - 02/09/09 06:54 PM Re: Question About Recessed Lights [Re: leland]
ChicoC10 Offline
Member

Registered: 05/30/07
Posts: 169
Loc: CA
We've been ICAT here in CA since the October 2005 revision of Title 24.

I just heard tell of old partner installing all 80 IC (non-AT) cans in a new residence. As it turns out the inspector will let him fly with just AT trims.

I've used both since the revision not knowing I had an option.
Just as well as I like the finished product better.

Top
#184417 - 02/09/09 08:03 PM Re: Question About Recessed Lights [Re: ChicoC10]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Still looking!

What a PITA. Ma Web sites.

Top
#184436 - 02/10/09 05:39 AM Re: Question About Recessed Lights [Re: leland]
George Little Offline
Member

Registered: 01/18/04
Posts: 1445
Loc: Michigan USA
I'm still checking also Leland, I should be getting something kinda official from Cooper Industries (Halo Lighting) on the compatibility and interchange of their trims with the cans.
_________________________
George Little

Top
#184463 - 02/10/09 08:53 PM Re: Question About Recessed Lights [Re: George Little]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 4904
Loc: Brick, NJ USA
George/Leland:

Went to Cooper/Halo website & poked around. I used the H7ICAT, and went to trims. 4 were on the spec page (trims) and 3 were OK for that can; 1 was not.

Looks like a spec sheet trail is going to be needed.

BTW, who checks to see if the gasket/caulk is properly installed after shtrock & before trims????

George, you're killin me