Am I correct in thinking that I should use the thhn/thwn #6 wire for my application described in the thread above? I want to do it right so I don't have to worry about it later. Thanks guys.

Joined: Jul 2007
Posts: 1,335
S
Member
Originally Posted by helpmepls
I want to do it right so I don't have to worry about it later.
This is always a plus

How longer is your feeder?


"Live Awesome!" - Kevin Carosa
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
With a 50a breaker you could use 8ga copper for this feeder at the 75c ampacity. It sounds like you will have fairly diverse loading. The other issue might be voltage drop if this is a long run.


Greg Fretwell
Joined: Aug 2008
Posts: 4
H
New Member
I decided to go with 6ga because the feeder is just about 100ft. My main concern was if the thhn/thwn copper was the correct type to use. I have had a lot of people tell me to just use the uf in the conduit if I was worried about the wet location, but that just wouldn't be right.

Joined: Jul 2007
Posts: 1,335
S
Member
don't forget to upsize your grounding conductor too since you are upsizing for Voltage drop (See note Table 250.122).