#179203 07/01/08 08:34 AM
Y
250 hp 480 volt three phase
302A
302x125%= 377.5 = 3-500mcm &Gr(per 250.122). 3 inch conduit
Breaker 600A.
125 Hp480 volt 3 phase
156 A
156x125%=195amps = 3-3/0 plus gr. 2 inch conduit
Breaker 250 amp
both either soft starts or VFD.
Wanna check my work guys.
Hair line between Pride & stupidy Right!!!
Tom Offline
Numbers look OK to me.
Can you send me some Pasties? I could send you some Pepperoni rolls in return.
Y
You mean the ones that go on yer Nipples.
JBD Offline
80-95% of the time my preference is to use soft starts for starting only applications and to save the VFD's for speed control.
Tom Offline
Yoopersup,
I thought you were a uper, not a loper & I mean the ones you eat.
What kind of breaker?
What environment? Wet? Dry?
What ambient temperature?
What type of insulation on the conductors?
No mention of overloads.
Details, Ernie, details- You know how I am.
George Little