Safety at heights?
1 members (Scott35), 527 guests, and 14 robots.
#179203 07/01/08 08:34 AM
Y
250 hp 480 volt three phase
302A
302x125%= 377.5 = 3-500mcm &Gr(per 250.122). 3 inch conduit
Breaker 600A.
125 Hp480 volt 3 phase
156 A
156x125%=195amps = 3-3/0 plus gr. 2 inch conduit
Breaker 250 amp
both either soft starts or VFD.
Wanna check my work guys.
Hair line between Pride & stupidy Right!!!
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
Tom Offline
Numbers look OK to me.
Can you send me some Pasties? I could send you some Pepperoni rolls in return.
Tom
Few things are harder to put up with than the annoyance of a good example.
Y
You mean the ones that go on yer Nipples.
JBD Offline
80-95% of the time my preference is to use soft starts for starting only applications and to save the VFD's for speed control.
Tom Offline
Yoopersup,
I thought you were a uper, not a loper & I mean the ones you eat.
Tom
What kind of breaker?
What environment? Wet? Dry?
What ambient temperature?
What type of insulation on the conductors?
No mention of overloads.
Details, Ernie, details- You know how I am.
George Little