Member
Where in the code does it say that the service disconnect and the OCPD has to be seperate? The intent of the code IMO is met. Outside of running up the cost to the owner, how would a seperate disconnect provide additional protection or safety? The NEC is only about safety, not future capacity, efficiency or convienience.


"Live Awesome!" - Kevin Carosa
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2003
Posts: 139
B
Member
Originally Posted by sparkyinak
Where in the code does it say that the service disconnect and the OCPD has to be seperate?


It doesn't ?

Quote
The intent of the code IMO is met. Outside of running up the cost to the owner, how would a seperate disconnect provide additional protection or safety? The NEC is only about safety, not future capacity, efficiency or convienience.


I realize that, however I am not asking if there needs to be a separate disconnecting means. There is no service disconnecting means for one service conductor? I don't see where that is permitted.

The actual soultion is really the instructions labeled on the panelboard enclosure. It clearly states that the unit is not suitable for use as service equipment unless a main breaker is installed or with 6 disconnects or less when not used as a lightning and appliance panelboard.

It is be used as a lightning and appliance panelboard therefore a main is required in order for the equipment to be used as a service.

This has been a rather interestng discussion. I have posted this question on four separate Forums and have received completely mixed answers of yes and no. All good arguements either way.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Jul 2007
Posts: 1,335
S
Member
230.79(A)


"Live Awesome!" - Kevin Carosa
Joined: Apr 2003
Posts: 139
B
Member
230.79 identifies the required rating of the service disconnecting means. There isn't one on the service I describe.

Or I should say, not one for ALL service conductors installed.

Last edited by BPHgravity; 04/11/08 09:50 PM.

Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Jul 2007
Posts: 1,335
S
Member
230.79(A) is for a single circuit service. If the is not applicable to your topic, what do you have that we do not know yet?


"Live Awesome!" - Kevin Carosa
Joined: Apr 2003
Posts: 139
B
Member
It's not a single circuit service. It's a 3-wire service.

Let's try another example. Say this was a 120/240V delta service. It is quite possible the B phase (208V) will have no loads at all. But, a service disconnecting means and overload device is required for that conductor. Right?

Back on my original question, doesn't 230.71(B) state that single pole units aren't permitted on multiwire circuits unless 2 or more are handle-tied together?

So again, where does the code allow service conductors to be installed and terminated at a panelboard without a disconnecting means and overload protection.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Mar 2005
Posts: 399
A
Member
I'll begin by saying I have approved many installations like this for Traffic signals etc.

To satisfy the exact Code would two 1P15 breakers with a handle tie and labeled service disconnect, and the load on only one of the breakers work ? (Waste of material)
If that is too complex just remove one of the line side conductors. (Cheapens the job)

I'm dealing with guys that want to bury MC cable. frown


Alan--
If it was easy, anyone could do it.
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
Terminate the second phase in the meter can, don't bring it to the panel, backfeed the 15a breaker with a clip and "Service disconnect" sticker. connect the load to another 15a breaker if you are a purist. (or the MLO lug? wink )


Greg Fretwell
Joined: Apr 2003
Posts: 139
B
Member
The solution Greg states is the way the manufacturer wants it done and the way I believe the code is worded.


Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
If the intent is that the service disconnect removes power from the panelboard rails (not an unreasonable interpretation) backfeeding the 15a breaker is the only way you can do it. The operative question would be, with a single connected load, could the load be directly connected to the MLO lug, protected by the "main".