Joined: Mar 2003
Posts: 849
Y
Member
I;ve seen Chase nipples put into the top of Mcc's (in wireways only) then several Tray cables run into them . I told the conmtractor I didn't feel this was a approved termintation method. I;ve seen Nipples from Mcc's up to the tray (lest them 24inches . But never Chase nipples?? My concern was even thought the nipples open into the wireways it leaves an unprotected opening.YER opinions Please.
YoopersUp

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I have seen what you describe. The wiring trough area of MCC's (for load conductors) does not provide direct access to any energized parts, I would be more concerned with securing the TC.

Joined: Mar 2003
Posts: 849
Y
Member
The drop from the tray to the Mcc's is only about 24-36 inches Max.what about 392.8(c)

Joined: Nov 2000
Posts: 2,148
R
Member
Take a look at 312.5(C) and 314.17(B).


Don(resqcapt19)
Joined: Mar 2003
Posts: 849
Y
Member
But does a MCC come into play in that section??

Joined: Nov 2000
Posts: 2,148
R
Member
In my opinion, between Articles 312 and 314, all electrical enclosures are covered.


Don(resqcapt19)
Joined: Mar 2003
Posts: 849
Y
Member
The Scope sections 312.1 & 314.1 says otherwise.

Joined: Nov 2000
Posts: 2,148
R
Member
I think that I can stretch the scope of 314 to cover just about any electrical enclosure including MCCs.


Don(resqcapt19)
Joined: Mar 2003
Posts: 849
Y
Member
314 No way. 312 you'd have to use 90.4 and I really think you'd be streaching it. Which one is it a Cabinet(see definitions) Cut out box (No), Meter Socket encloser (No).
So then a MCC must be a Cabinet .
Cabinet (an encloser that is designed for either surface mounting or flush mounting and is provided with a frame ,mat, or trim in which a swinging door or doors are or can be hung. Doesn;t sound like a MCC does it??

Joined: Nov 2000
Posts: 2,148
R
Member
The part of the MCC that you run the cables into is used as a pull box.
Quote
314.1 Scope
This article covers the installation and use of all boxes and conduit bodies used as outlet, device, junction, or pull boxes, depending on their use, and handhole enclosures.


Don(resqcapt19)