ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 567 guests, and 39 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 3 of 3 1 2 3
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
There usually is a ground rod at each pole, certainly any pole with a transformer on it. I find little difference electrically between the service drops and a feeder to a separate building. I suspect that is why 230 and 225 have so much similar language. The only significant difference is the lack of overcurrent protection of service conductors and that really doesn't affect the point and method of grounding that much IMHO, only the grounding conductor size (250.66 vs 250.122).
From a lightning and surge standpoint, separating the neutral and ground at a remote site is troublesome. The only way to "stabilize the voltage to earth" is via your TVSS equipment and that will have a significant "let through" voltage before it triggers.


Greg Fretwell
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Oct 2007
Posts: 27
N
Member
So in my case, with wires coming from a remote meter disconnect, I would be better off leaving out the ground wire and driving a couple of rods? I was going to drive the two rods anyway. This would allow me to not have to rewire the panel (seperate the grounds and neutrals to seperate bars). The only things coming to the house are phone and cable, directly from the pole. Sounds like a better way to go. One less wire to pull, I'll use the #3 elsewhere.

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
You need to drive the rods in either case. You must have a local connection to the earth for anything but a single branch circuit. I think 3 wire vs 4 is better for your electronics but that might just be me wink