Does the electrical utility in your area install a second grounded conductor from their transformer to the service equipment?
I've read some posts on other sites stating such is the case in some areas of the country. Isn't that a CODE VIOLATION? Creating a parallel path from the service equipment back to the transformer. What's up with that? [Linked Image]
#1543 05/16/01 02:20 PM
Anonymous
Unregistered
Why would it be a code violation?
I would call it a good thing.
Parallel conductors per se are not code violations.
If you want to run three wire cable through you house and use two for neutral and one for hot, that is okay.
Parallel conductors are a violation when current can follow a return path that is not parallel to the feed path.
Besides, a parallel path already exists through the earth back to the transformer anyway.
#1544 05/16/01 02:53 PM
Dspark,
What about 310-4???
#1545 05/16/01 03:07 PM
Hmmm... Good one...!?!
However, I see it as a good thing to provide a redundant GC to prevent the "lost neutral 240 V series" scenario.
Common sense vs. NEC?
-Virgil
5 Star Inspections
Member IAEI
#1546 05/16/01 03:49 PM
Mike Offline OP
It's not a code violation if all the conductors are paralled. From the stories I read, it's only the GC that's paralled. If the utility insists on a paralled GC, not the ungrounded conductors, all the why to the service equipment. I have a problem with it. IHMO. [Linked Image]
#1547 05/16/01 03:53 PM
Anonymous
Unregistered
>What about 310-4???
Doesn't that just confirm that extra neutrals (parallel) are a good thing when used correctly?!?
I mentioned in another thread that 200% neutrals are specified for certain newer installations.
http://www.electrician.com/articles/third.htm
Are you suggesting that these might be illegal?
[This message has been edited by Dspark (edited 05-16-2001).]
#1548 05/16/01 03:58 PM
Anonymous
Unregistered
I don't believe it is a code violation if only one of the conductors is paralleled.
The intent is that conductors do not have to have the same characteristics.
I can't think of a problem with having parallel neutrals. If you have a problem with them, kindly explain. If you have a hypothetical scenario, that is even better.
#1549 05/16/01 04:27 PM
Dspark,
I miss read the original post. I thought we were talking about paralleling the grounded conductor and an equipment grounding conductor. The is no problem with parallel neutrals.
#1550 05/16/01 04:33 PM
Dspark,
parrallel all you like, 1/0 & up [Linked Image]
Mike;
other posts have really got in depth with this, if you think about it, a lot of our concerns are addressed by having a
ground(ing) & ground(ed) conductor back to the X-former.
heck ,we gotta do it for a SDS x-former!
besides, they don't ( to my knowledge) make 3000 kcmil .....
[This message has been edited by sparky (edited 05-16-2001).]
#1551 05/16/01 05:28 PM
Anonymous
Unregistered
>parallel all you like, 1/0 & up
And smaller for neutrals. http://www.electrician.com/articles/third.htm