0 members (),
516
guests, and
17
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
Does the Building code require Metal venting for Dryers? (Residential Occupancy) Or is that a Manufacturer's recomendation?
Bill
Bill
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I'm pretty sure the IRC requires it except at the appliance. I'll check tommorrow for you.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Hi Bill. Section M1501.1 of the 2000 IRC states that the duct shall be metal.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Is that solid ducting, or the Spiral-wound expanding type? The latter is very common here for dryer vents and such like.
|
|
|
|
Joined: Feb 2003
Posts: 67
Member
|
bill, the umc section 504.3.2.1 says"domestic clothes dryer moisture exhaust ducts shall be of metal and shall have smooth interior surfaces"exception allows up to 6' of approved flexible duct to connect to the metal duct.flexible portion not to be concealed.
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
How new is this requirement?
I can swear there's still plastic dryer venting kits on the store shelves, or that there was recently.
Bill
Bill
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Bill: I'm not sure how new this requirement is, sorry.
In regards to your statement about product availability, this should not surprise you. Take a trip some time to a big box (or other) hardware store and see how many non-compliant items you find. The plumbing department, for example, has many, many items that do not comply.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
OP
Member
|
How many Electricians among us install the venting for Dryers and Exhaust Fans?
I've always maintained that it really wasn't my job and would only do it if no one else would or could. What have you seen, who usually does it?
Bill Addiss
[This message has been edited by Bill Addiss (edited 12-17-2003).]
Bill
|
|
|
|
Joined: Oct 2001
Posts: 597
Member
|
In my area, venting requires a seperate permit. The owner-occupant or an HVAC contractor are the credentials required to pull the permit.
Al Hildenbrand
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I have never done the venting, I may supply the exhaust fan but not the venting. I only see the HVAC guys do that or once in a while the GC.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 75
Joined: June 2012
|
|
|
|