Hello
My name is Dave Jackson, I work in the papermaking industry and am a Safety Rep. I have a question that some of your members may be able to answer.
Is there a minimum standard of design for electrical isolation points? Some of the ones we have in my workplace, I believe, are not up to standard. There are a few where an operative is able to attach a lock whilst the
switch is still in the 'ON' position. Surely this cannot be right. I would be grateful if anyone can advise me on the appropriate designs.
Thank you
Dave Jackson
PS. I believe Dave is from the UK
[This message has been edited by Webmaster (edited 05-14-2003).]
Dave,
No being 100% sure where you are located and what standards would apply to you, I will base my response in general terms, trying to to reference OSHA too often.
In general terms, any isolation device must be capable of with standing the magnitude of energy the source is capable of. As for the location of the lock or tag, there are some cases where the equipment would need to be locked in the on position for other reasons, some of which are safety related. This differs from Lockout in which we lock energy isolating devices in the safe position, which is usually in the open/off position. In your industry, there are times when a piece of equipment is reffered to as "critical equipment". This would be equipment such as colling water pumps, emergency quench pumps, etc. By applying a lock to the controls for this critical equipment, you are somewhat assured that when the equipment is called upon to funtion, that it will indeed do so. In the states, we do what is called "car-sealing" in which we hang a tag on a non-resuable, self locking plastics tab tomake sure the equipment/device remains in the safe posiiton. Breaking a "car-seal" takes an act of congress, as if it is not returned to the proper position, a serious accident is highly possible. All of this could explain why you ahve equipment that is capable of being locked in the on position.
With that said, I MUST ALSO say that this function and LOCKOUT are two different animals and in most cases, the switches used in "critical equipment" control are in no way made for lockout/tagout. If you are in the USA, OSHA clearly states that control switch and control circuitry can NOT be used as an isolation device. This is for several reasons, but the simplest reason is this is where you will be testing to see if you got the energy source to ZERO energy. if you locked out the switch, verifying ZERO energy becomes an electricians job, as you would no longer have your switch to test the energy source.
Is all of this making sense???? Bottom line, I would be very skeptical of a switch that is designed to be capable of being locked out in the ON position; especially if the energy source(s) is electrical or mechanical. If I were in your shoes I would call the vendor and inquire about the proper energy isoaltion points for the equipment.
Bryan Haywood www.SAFTENG.net
Bryan,
In some places, the use of an isolator that can "also" be locked in the ON position, is to prevent the likelihood of tampering.
Even so, I've never liked the idea of not being able to turn off a piece of equipment, especially in an emergency!.
Fire sprinkler pumps and smoke control systems would be a notable exception though!. [Linked Image]