Who determines if a structual metal member in an existing building is "effectively grounded"? (NEC 250.52(A)(2) Is there a particular test performed to decide?
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Frank: I guess it depends on who is asking, or requesting the bonding info. The electrical contractor has the NEC responsibility in new construction, and major renovation work here. THe iron workers make-up "tight" connections, and we bond to the main beams usually. If the client, architect, engineer, etc. specs or requests, we install jumpers as specified.
John
John
|
|
|
|
Joined: Jul 2001
Posts: 311
OP
Member
|
HotLine1-
Typically, where are the jumpers normally installed?
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
Frank, You can get IAEI Soares book on grounding for a very thorough explanation. If the steel is attached to bolts, in concrete, underground, it is basically considered grounded. It can get more complicated and I suggest a good read of Soares.
All steel needs to be bonded to the neutral though, don't forget that.
jumpers do not need to be attached for continuity, only welded or bolted together, and that usually is accomplished by the steel guys.
|
|
|
|
Joined: Jul 2001
Posts: 311
OP
Member
|
Thank you for responses. I'm meeting with an Electrical Engineer at job site this morning. Briefly, a separtely derived system is going to be installed on the eighth floor of our City Hall Building for County wide Court system. It is going to provide power for a computer room. Running a grounding electrode conductor to the water meter in the basement is one option. Of course a ground rod must be driven. The other option is to use the structural building steel which does not require a driven ground rod.
Frank
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Frank,
250.30(A)(4) specifies that it shall be the nearest of the two (eff. grounded structural steel or water pipe) that is used.
The way I read it a rod is not required either way if the steel or water pipe is available/used per 250.30(A)(4)(3)
Bill
[This message has been edited by Bill Addiss (edited 09-20-2002).]
Bill
|
|
|
|
Joined: Jul 2001
Posts: 311
OP
Member
|
Bill-
The Electrical Engineer deemed the structural metal not effecively grounded. He wants to use the metal water pipe. Wouldn't 250.53(D)(2) apply. ie. Supplemental electrode required, or doesn't that apply for separately derived systems?
Frank
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Frank,
I read it that the rod is not required in this case (per 250.30(A)(4)(3) ) if you use the steel or the water pipe within 5 ft of point of entrance ro the Building. Does anyone else agree?
Bill
Bill
|
|
|
|
Joined: Aug 2002
Posts: 36
Member
|
|
|
|
|
Joined: Jul 2001
Posts: 311
OP
Member
|
Bill-
I have to continue to research this. I guess the basic question is: When using a metal water pipe for a grounding electrode for all Code applications, is a supplemental electrode required?
Frank
|
|
|
Posts: 7,382
Joined: April 2002
|
|
|
|