1 members (Scott35), 522 guests, and 41 robots.
#137080 05/25/03 06:56 PM
There is a requirement in the UK to bond the lighning conductor to the electrical installations main earth terminal. I cannot see any advantage in this, any comments?
regards
lyle dunn
#137081 05/26/03 02:24 PM
Lyledunn,
In regard to your enquiry, i have never had to bond a lightning conductor to the main earthing terminal of any installations here in England,
I will look up the relevant codes in regard to this but i am sure we dont have to,
most of the specialist companies take a lighting conductor staight to the ground, i cannot see any point in linking it to the main earth conductor.
John H
#137082 05/26/03 02:35 PM
Most bonding requirements are to make sure that a mimimum of potential difference can exist between exposed metalwork in the event of a fault (or in this case, a lightning strike).
I have to admit that I'd need to check this point myself, as I've never yet worked on any building with a lightning rod.
Certainly when installing radio masts and such like, I would always securely ground and bond the mast.
#137083 05/26/03 03:40 PM
Yes you do have to bond lightning protective system, see Reg. 413-02-02 (vi) in BS 7671: 2001.
#137084 05/27/03 02:21 PM
I have not came across this myself, but have recently observed a new bank of mobile phone masts being installed in the grounds of my work place and noticed they ran there lightining conductor (which was i noticed, insulated?) straight onto there own earth rod!
Is it a good idea to introduce such high voltages towards an earthing system which is not struck?
#137085 05/27/03 03:10 PM
C-H Offline
I think I've seen this too. Alongside the electrical panels on this floor, there are bundles of cables going up to the roof where there are a lot of antennas. Among the wires is a thick green/yellow wire, which I assume is a lightning conductor.
Despite the fact that ordinary lightning conductors are bare and run close to buildings, they protect the building. I guess the insulation can be there simply to keep people from touching the wire, i.e. not introducing a shock hazard beacause of different potentials.
OTOH, the insulation on the wire can withstand a higher voltage than normal for the very short period a lightning lasts and if the lightning has a good path to earth, it is not going to jump to find another path.
(Personally, I still don't like it. I think the conductor it has to withstand hundreds of kilovolts, something which requires several millimetres of insulation. But then, I'm just a student who doesn't know this field.)
[This message has been edited by C-H (edited 05-27-2003).]
#137086 05/27/03 06:45 PM
Thanks to all.
Paul, I fully realise the purpose of equipotential bonding conductors as minimising fault voltages between exposed and extraneous conductive parts within the so-called equipotential zone. However, I am not convinced that there is any valuable purpose served in this respect by connecting to the lightning conductor. Equally, on loss of neutral on a TNCS system it would actually be better if the lighning conductor was separated from the MET. In fact imagine that all BS7671 requirements were met and that some guy was about to test the down conductor. So he separates the down conductor from the earth electrode. At that moment a fault occurs in some circuit in the installation which will raise the potential at the MET with respect to earth.The same voltage will appear at the disconnected down conductor with respect to earth. A rareity perhaps but nonetheless a distinct danger!
regards
lyle dunn
#137087 05/30/03 10:32 PM
Lyle,
I would not personally use the mains earth as a Lightning conductor Earthing point.
I would instead drive a seperate electrode for this.
The reason for this being, while lightning has a reasonably high voltage, it has an even higher current (500kA) and introducing this level of current into an Electrical system, no matter how good the Earthing connections are, is not really my idea of a good time.
