1 members (Scott35), 355 guests, and 38 robots.
#128241 12/03/02 01:54 AM
Y
yu Offline OP
Hi, needs advice here. What is the different between Line and Source Impedance? A 3-phase x-ray machine is running at 200mA ~ 500mA instead of maximum of 800mA which i suspect is due to cable size. Requirement for X-ray Source impedance is 0.12 ohms. I got the readings on a report as this: RY-0.233, YB-0.239, BR-0.225. Can anybody explain why RY instead of R or Y or B?
tq.
#128242 12/03/02 01:32 PM
About "...readings on a report as this: RY-0.233, YB-0.239, BR-0.225." What are the units for these numbers? How were these measured or determined?
#128243 12/05/02 01:19 PM
yu, if I understand correctly, the measured impedance is roughly double what is desired.
Components that most affect impedance are the circuit’s cable size and length, and serving transformer size {impedance.} Each would effect voltage drop on a circuit.
The only solutions I can imagine are 1.) increasing the size or cross-sectional area of the cables, [likely least expensive, but with a potentially limited improvement] 2.) shortening the circuit length [probably not practical] or 3.) installing a larger [lower-impedance/expensive] serving transformer. These three items are probably at least 90% of what effects source impedance on a branch circuit or feeder.
Tests to determine the change {or improvement} from cable replacement may be to carefully apply the instrument at the feeder level if the circuit of interest is indeed a branch circuit, and then at the serving transformer’s secondary terminals.
I hope that answers your question or confirms your suspicions.
