#124201 09/02/06 09:39 PM
Trumpy Offline OP
All pictures and information supplied by RODALCO:
500 kVA, 11 kV / 230 / 400 Volts Transformer at Orbit road Albany TB 2163
Jumpers were 120 mm² Copper
I had to adjust a streetlight timeclock.
When I opened the door I smelled burning and hot plastics.
I took the photo's and closed the door, did not want to disturb anything in case a phase to phase flashover occurred.
Arranged an emergency shutdown to upgrade the jumpers.
New 240 mm² jumpers were put in that evening.
Next day I took a load check and measurements were as listed.
Load on Red phase 600 Amps
Yellow Phase 470 Amps
Blue Phase 440 Amps
Still within the 500 kVA rating which is 696 Amps per phase.
Currently there are another 2 big buildings nearing completion. the transformer will be upgraded to 750 or 1000 kVA.
Regards
Raymond
The pics:
Thank you Ray!. [Linked Image]
#124202 09/03/06 12:16 AM
From the second pic, looks like some sort of fault has already happened in there, notice the blackening of the can to the right of the streetlight block?
Are those factory installed jumpers? If so they should have been adequate for the full rated load. [Linked Image]
But I also see this stirring up the debate on bundling!! [Linked Image]
I would have been wary of disturbing anything too. [Linked Image]
Stupid should be painful.
#124203 09/03/06 12:48 AM
No not as far as i'm aware off mxslick.
These cables are NOT factory installed.
These DIN racks are assembled and put in on site by whoever gets the quote for the transformer install.
These cables were obviously under rated and should have been upgraded when other DIN fuses were loaded to accomodate new circuits.
In stead of doing it correctly the first time, Jumpers should be adequate for the maximum continuous load + 20 % from the transformer.
In this case cables rated at 800 Ampères should have been fitted. Better to feed the busbars from two sides as well.
Note the red colour sleeve by the bushing which has split from heat transfer from the copper conductor.
Bundling too, cables close together can't dissipate heat as effective. Better to use insulated spacers in between them.
#124204 09/03/06 01:00 AM
Looks like the ampere readings you took are obviously accurate, one look at those jumpers and you can see that the red phase is definitely the high leg. Way to go on diffusing that ticking timebomb Raymond.
Luke Clarke
Electrical Planner for TVA.
#124205 09/03/06 01:36 AM
What's that small wire that appears to be loosely attached to the black bus(position #4)?
steve
Steve
#124206 09/03/06 03:53 AM
Trumpy Offline OP
Steve,
That would be a temporary neutral. [Linked Image]
#124207 09/03/06 07:55 AM
A temporary Neutral stamcon
That one and the red phase one with the airborne HRC fuse are driving the (temporary) timeclock,
which drives a streetlight contactor below the five 16 amps HRC fuses.
#124208 09/04/06 04:47 PM
Trumpy Offline OP
Our Neutrals are Black here in NZ.
Good skills though Ray, leave the thing to cool down before doing anything with it.
I see the heat-shrink cover has split, it takes a bit to do that.
One of your own time clocks?.
I note the RF label on the clock panel.
One thing I have noticed since leaving the PoCo here in Ashburton, is that sometimes on Monday nights, the Street-lights are out.
Not one block, but most of the town.
Un-real!.
#124209 09/05/06 01:46 AM
Well spotted Mike,
I use RF 9xx asset numbers on the clocks and an XL spread sheet to keep track of my clocks, platform numbers, address etc.
That is one of the newer ones. Late 1988 Maxirex BQT from Germany.
A lot of clocks I use are 40 + years old with full clock work motor driven mechanisms. (Landis&Gyr, AEG, Sangamo).
Mike, the POCO obviously needs you back and is lacking qualified staff to deal with the streetlights matter.
edited for typo's RF.
[This message has been edited by RODALCO (edited 09-05-2006).]
#124210 09/21/06 09:14 PM
I know this is minor compared to the problem at hand but i dont like the zipties, too tight. Just makes the heating worse.