0 members (),
171
guests, and
31
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
I inherited a small industrial a couple years ago and am still learning their system. I would like to know what this yellow box is. The CT metering is in a small substation ahead of this point so that eliminates a CT cabinet. There are no apparent openings other than for the cables entering and leaving. The service is 480/277 Wye. I believe this is part of the original serivce to the building built 50+ years ago. The serving utility and the industrial disagree on who owns the 3- 500kva transformers in the sub outside. Neither claim ownership. They do agree that any work from the load side of the transformers on in, is the industrials responsibility which trickles down to me. Tom Noller
|
|
|
|
Joined: Oct 2004
Posts: 806
Member
|
Tom:
I'd put my guess on that box holding power factor correction capacitors.
Would you be able to get close enough to see or get a pic of any data plates?
Stupid should be painful.
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
i think more like a disconnection or isloation switch without fuse in there one of the two hard to say but if it have lever on it then good chace that is disconnection switch
merci , marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Nov 2005
Posts: 2
Junior Member
|
No tags, no handles. I am leaning towards the power factor correction capacitor but until we shut down the sub later this winter I won't be getting close enough to open or exam closer. If it is a capacitor bank they must not be working because we had to add 100KVAR last year. Plant power factor went from 70s to 98. Thought the manager was going to kiss me.
|
|
|
|
Joined: May 2001
Posts: 717
Member
|
I don't think I'd bet here without much closer observation, but it looks like an automatic recloser.
|
|
|
|
Joined: Dec 2005
Posts: 869 Likes: 4
Member
|
Strange that where the nameplate is supposed to be, nothing attached there.
The yellow paint looks too good. I think that it never had a nameplate on it.
A auto recloser normally has some id number on it. Although its likely to be something like that.
a capacitor normally wouldn't have cables coming in and out at both sides.
The product of rotation, excitation and flux produces electricty.
|
|
|
Posts: 524
Joined: December 2003
|
|
|
|
|