I got a violation notice on a ground bar. (The picture I took of it came out bad, though, so here's one just like it). I slipped up and told the inspector he was crazy...Oooops It's a factory supplied component for a Cutler-Hammer 225 Amp Main Lug panel. Now, what's the matter with it?
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Hello Scott, I slipped up and told the inspector he was crazy...Oooops doesn't that come under the heading of s---happens? The only thing I can think of is he wants a green screw or nut. Of course you could tell him that besides his being crazy, until a conductor is landed on the bar it doesn't exist. Roger
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
What doesn't he like about it?
If this was a factor installed bar wouldn't any changes you make to it possibly void the UL listing?
I think you were being nice. I would have said more than calling him crazy.
Curt
Curt Swartz
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Some people have a hair across it, and should be told so! (politely of course...)
Raise one brow like Spock, and a calm monotone voice... "I'm sorry, but you are out of your mind"
I had a simular thing happen with a panel once, the Inspector made some wild claim about "modification" of a neutral buss. So we continued with the Inspection, while I sent a guy to the supply house to get another one. He came back, we opened the un-opened box in front of him. Then took it back, a waste of time and money......
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Feb 2004
Posts: 1,438
Member
|
Scott, Was it a new, overly zealous inspector that I might be dealing with in a coastal city? I've got one that wrote a subpanel I changed up as this exactly "Continuity problem at subpanel" Thats all he wrote! I called him & he said between the neutral & ground there's a continuity problem... I measured it & it rang out just fine... I recalled him out.... We'll see if he's really crazy -Randy
|
|
|
|
Joined: Dec 2000
Posts: 4,294
OP
Member
|
The reason he wrote it up is that this mounting does not provide "direct metal contact."He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub. He says that the hole (7/8", 1-1/8", etc) is larger than the fitting, and thus does not provide "direct metal contact". I looked up "direct metal contact" in the '99 NEC for a total of 0 hits for my query. The secondary conductors from the utility transformer were not yet installed, so when I gave him a torque letter from the office that the gear had been torqued to specs, he told me I was committing FRAUD. This & more was all before I told him he was crazy. ...S He's an older fellow not by the beach, Randy.
|
|
|
|
Joined: Jul 2004
Posts: 200
Member
|
Some people have a hair across it, and should be told so! LMFAO!!!! Inspectors???
If hindsight were foresight, we'd all be millionaires!
|
|
|
|
Joined: Sep 2003
Posts: 123
Member
|
I see it, its that ag, with the green writing, its partly under the attachment nut. It must be interfering with the "direct metal contact". Or was that direct mental defect??
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub. I will steal a line from electricmanscott. "Poor fellow"Did you explain to him that no one gives a .... about what he likes?
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 44