506
19
I got a violation notice on a ground bar. (The picture I took of it came out bad, though, so here's one just like it). I slipped up and told the inspector he was crazy...Oooops It's a factory supplied component for a Cutler-Hammer 225 Amp Main Lug panel. Now, what's the matter with it?
Hello Scott, I slipped up and told the inspector he was crazy...Oooops doesn't that come under the heading of s---happens? The only thing I can think of is he wants a green screw or nut. Of course you could tell him that besides his being crazy, until a conductor is landed on the bar it doesn't exist. Roger
What doesn't he like about it?
If this was a factor installed bar wouldn't any changes you make to it possibly void the UL listing?
I think you were being nice. I would have said more than calling him crazy.
Curt
Curt Swartz
Some people have a hair across it, and should be told so! (politely of course...)
Raise one brow like Spock, and a calm monotone voice... "I'm sorry, but you are out of your mind"
I had a simular thing happen with a panel once, the Inspector made some wild claim about "modification" of a neutral buss. So we continued with the Inspection, while I sent a guy to the supply house to get another one. He came back, we opened the un-opened box in front of him. Then took it back, a waste of time and money......
Scott, Was it a new, overly zealous inspector that I might be dealing with in a coastal city? I've got one that wrote a subpanel I changed up as this exactly "Continuity problem at subpanel" Thats all he wrote! I called him & he said between the neutral & ground there's a continuity problem... I measured it & it rang out just fine... I recalled him out.... We'll see if he's really crazy -Randy
The reason he wrote it up is that this mounting does not provide "direct metal contact."He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub. He says that the hole (7/8", 1-1/8", etc) is larger than the fitting, and thus does not provide "direct metal contact". I looked up "direct metal contact" in the '99 NEC for a total of 0 hits for my query. The secondary conductors from the utility transformer were not yet installed, so when I gave him a torque letter from the office that the gear had been torqued to specs, he told me I was committing FRAUD. This & more was all before I told him he was crazy. ...S He's an older fellow not by the beach, Randy.
Some people have a hair across it, and should be told so! LMFAO!!!! Inspectors???
I see it, its that ag, with the green writing, its partly under the attachment nut. It must be interfering with the "direct metal contact". Or was that direct mental defect??
He also doesn't like the EMT fittings without a grounding bushing or a Meyers Hub. I will steal a line from electricmanscott. "Poor fellow"Did you explain to him that no one gives a .... about what he likes?