This was discussed via another issue recently. Let the games begin! 230.70 If this gave you a footage as a maximum, you would have something to fall bak on, and be able to "No, won't do it!" Commentary from the handbook: No maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this Code has the responsibility for, and is charged with, making the decision as to how far inside the building the service-entrance conductors are allowed to travel to the main disconnecting means. The length of service-entrance conductors should be kept to a minimum inside buildings, because power utilities provide limited overcurrent protection and, in the event of a fault, the service conductors could ignite nearby combustible materials. Some local jurisdictions have ordinances that allow service-entrance conductors to run within the building up to a specified length to terminate at the disconnecting means. The authority having jurisdiction may permit service conductors to bypass fuel storage tanks or gas meters and the like, permitting the service disconnecting means to be located in a readily accessible location. However, if the authority judges the distance as being excessive, the disconnecting means may be required to be located on the outside of the building or near the building at a readily accessible location that is not necessarily nearest the point of entrance of the conductors. Also see: https://www.electrical-contractor.net/ubb/Forum4/HTML/000367.html As for the wire size.... What's with that?
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jul 2004
Posts: 41
Member
|
The code states nearest point of entrance. The handbook is a 3rd party opinion and a helpful guide. But some don't respect the wealth of knowledge inside although not law (unless your juristiction adopted into law along with the code. Most AHJ have ammendments for specfic distantances. State of TN is 2'Max. Metro Nashville is 5'Max and is law by authority of the city council and 100% enforcable. In extreame cases for those who will not attempt to comply, They may be cited to the board for a licese hearing or stop work order the site and shut it down.
Kenny Wilee
|
|
|
|
Joined: Apr 2002
Posts: 2,527
Moderator
|
This raises a very good point. As for "done by city workers," it sounds like an installation by unqualified individuals that may very well skirt inspection. That is [or should be] criminal.
Some operations are such that electrical work does not undergo routine inspection. In that case, the electrician is ethically bound to use extra effort and education on their own initiative to police their own work, and make the finished job thoroughly “antiseptic” and well beyond minimums from a compliance standpoint.
|
|
|
|
Joined: Jul 2003
Posts: 394
Member
|
I suspect there is a lot of abuse by governmental agencies. I spent a couple of years working for a company/municipality. The town limits enclosed a shopping center, 5 houses, and an amusment park. One family owned all the land and leased to the shopping center. As for the rest, I was paid by the company but did anything the "town" needed. The state inspectors would wander in occasionally and tell us we shouldn't be doing what we were. We'd say OK and go somewhere else until they left then go finish the original job. We were open to the public so they could look around but since the town did not invite them in, they were pretty powerless. I learned a lot there. we owned the substation and all the distribution.
|
|
|
|
Joined: Aug 2004
Posts: 5
Junior Member
|
I don't think this meets anyone's definition of "nearest point of entrance". Looks to me like we also need to bond the isolated piece of metallic conduit.
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
In this case I would not permit this installation, regardless of what the handbook says. During a fire or future construction, who knows where those unprotected service conductors may be. My opinion, find another route.
Pierre
Pierre Belarge
|
|
|
|
Joined: Oct 2001
Posts: 18
Member
|
The POCO I work for wouldn't allow this. The LB's ahead of the meter could be tapped into for free power. Will the LB's be accessible after the finish work? What about bonding the metalalic mast and the meter can?
kduke
|
|
|
Posts: 3,682
Joined: October 2000
|
|
|
|