529
39
Posts: 2,236 Likes: 1
Got another relatively small problem with the "problem" house. The ex-EC left us with octagonal boxes in the shower stalls... the stalls are tiled, and enclosed in glass. The only thing I know of acceptable is recessed cans with wet-location-listed trims on GFCI protection... Any ideas out there? We're gonna have to cut tile for recessed cans, aren't we.... [This message has been edited by sparky66wv (edited 07-15-2002).]
Posts: 440 Likes: 3
66, This problem gets worse everytime I hear about it. I hate to say it, but I would cut the tile, and install cans. Look at the bright side. This is a T&M job.
Snickering, Doc
The Watt Doctor Altura Cogen Channelview, TX
or place an led in the octogon, and cover with a shower rated clear blank plate???
The NEC does NOT prohibit surface mounted light fixtures in the shower area. Look at 410.4(D) as Blackhat mentioned above. As log as you install a fixture rated for wet locations it would be just as acceptable as a recessed fixture. The height restrictions only apply to cord-connected, hanging, tracks, pendants and paddle fans.
Curt
Curt Swartz
Posts: 440 Likes: 3
I'm with you caselec, and blackhat. I think the point that 66 is trying to make is, that it is not the "normal" thing to do. I think that you will agree that most of the time shower lights are recessed can fixtures. They are in the residential applications that I've dealt with.
wageoghe, I didn't check your link, but my experience with lucifer lighting is that it is high dollar. I'm not saying that it isn't a good line of fixtures. Just get out your wallet.
Still snickering, Doc
Virgil,
Time to get out the roro-zip, goggles, earmuffs, and facemask!
A surface-mount fixture--ja! How about an A-lamp in a glass dome? IF the owner's into the industrial look, one with the guard/cage over the dome...
But seriously, I hope that eventually the GCs in your neck o' the woods who want things done right (from the start) will bring you in at the start...
Best regards to you & Musser--
Cliff
Posts: 7,382 Likes: 7
Sparky: Look in the RUUD Ltg Catalog, or RuudLighting.Com. They have a 12" square surface mount fluorescent that is 3R listed. 28 watt, electronic ballast, & gaskets to mount it.
Also, how "good" is the tile cuts around the box??? Can you get a Halo 4" recess in there??
HotLine1 John