#112117 - 03/15/01 10:11 PM Wire over Public Pool
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3006
Loc: NY, USA

City of Pittsburgh public swimming pool. The security camera cable run above the swimming pool appears to be in violation of NEC section 680.8....."Overhead Conductor Clearances". According to the 1999 NEC Code
Handbook (McGraw-Hill), the exceptions are only for Utility Company lines provided the clearance dimensions in Table 680.8 are observed.

Frank Cinker
Pittsburgh, PA

Top
#112118 - 03/18/01 06:51 AM Re: Wire over Public Pool
electure Offline

Moderator
Member

Registered: 12/24/00
Posts: 3978
Loc: Fullerton, CA USA
By the 1999 NEC,there's an exception for CATV coaxial cables to have a clearance of 10 feet if they comply with Art. 820. If this is a security camera, it is CCTV, and doesn't comply, but I can't see that there would be a difference in the safety aspect. What do you think?
Realistically, the installer should have carried something larger than an 8' ladder.

Top
#112119 - 03/18/01 10:35 AM Re: Wire over Public Pool
cinkerf Offline
Member

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
electure,

I feel there would not be a difference in the safety aspect. However, as you stated, it does not compy with NEC.

Frank (cinkerf)