Posted By: Admin Wire over Public Pool - 03/16/01 05:11 AM
[Linked Image]
City of Pittsburgh public swimming pool. The security camera cable run above the swimming pool appears to be in violation of NEC section 680.8....."Overhead Conductor Clearances". According to the 1999 NEC Code
Handbook (McGraw-Hill), the exceptions are only for Utility Company lines provided the clearance dimensions in Table 680.8 are observed.

Frank Cinker
Pittsburgh, PA
Posted By: electure Re: Wire over Public Pool - 03/18/01 01:51 PM
By the 1999 NEC,there's an exception for CATV coaxial cables to have a clearance of 10 feet if they comply with Art. 820. If this is a security camera, it is CCTV, and doesn't comply, but I can't see that there would be a difference in the safety aspect. What do you think?
Realistically, the installer should have carried something larger than an 8' ladder.
Posted By: cinkerf Re: Wire over Public Pool - 03/18/01 05:35 PM
electure,

I feel there would not be a difference in the safety aspect. However, as you stated, it does not compy with NEC.

Frank (cinkerf)