Wow.
It's not as if a double pole 30 amp Sq D circuit breaker is is impossible to find and install.
It looks like it took more work to thread those screw holes than it would have to make a proper install.
|
|
|
|
Joined: Jan 2005
Posts: 155
Member
|
ShockMe77, I agree but then there would have been no challenge. Just think of the thought that went into this. I bet the guy was proud of the way he solved his problem. Give the guy some credit for being an original thinker. It would be interesting to know how many people have lost their lives because of such installations and how many have been just plain lucky that similar work such as this hasn't failed......yet.
|
|
|
|
Joined: Apr 2003
Posts: 60
Member
|
I sure would not have wanted to be the one to close in that disconnect when it shorted. Guy must have jumped 20 feet straight back, IF he was able to let go of the handle!
|
|
|
|
Joined: May 2005
Posts: 178
Member
|
Two things I don't understand:
Why did the neutrals at the top of the panel burn? They don't seem to be related to the disconnect in any way, so I'm thinking they're the result of a separate incident.
Since the disco wires themselves aren't burned, I'd guess that the panel main CB tripped quickly, helped by the very short wire run to the disco. If it hadn't, this could have been a nasty fire.
But what caused the disco bar to short to the screw terminals in the first place? I suspect that the insulating parts between the bar and the knives failed and/or disintegrated due to the water damage, allowing the bar to rotate in deeper and hit the screws. If the handle has an overcenter "snap" spring, all this may actually have happened completely unattended.
I'd have to say that any disconnect that can fail in this way, regardless of damage, is of an unforgivably bad design.
Oh yeah, and the guy who screwed those wires to the buses is an idiot.
|
|
|
|
Joined: Mar 2005
Posts: 399
Member
|
It has been some years since i took these pictures but, if I rememeber right the neutrals burned because it was bonded at the disconnect and acted as the fault path to the CB panel. The rusted ground bar at the panel made a high resistance fault which heated the wires before the main tripped. Pressboard insulators on the movable jaws and switch arm fell apart due to the water. The screws at the panel is what made this a memorable installation. Alan--