0 members (), 433 guests, and 18 robots.
#108866 12/29/03 01:07 PM
Here's a reply I received from Bussmann:
Hi Joe,
It appears one of the members properly identified the product which we offer.
We offer "dummy" fuses or neutrals for Class H/R, Class CC, midgets (13/32" X 1-1/2") and small dimension (1/4" X 1-1/4") fuses.
These fuses can only be utilized where overcurrent protection is not required by the code, such as for neutrals.
For example, let's say you have a 120/240V system and use a 3 pole 240V switch.
You could run the two hot phases through two of the poles with protection by a fuse and install the "dummy" fuse in one pole, and run the neutral through.
They also use these allot in lighting circuits for the neutral conductor.
Bussmann
#108867 12/29/03 01:12 PM
Here are those "Dummy Fuses"
[Linked Image from bussmann.com]
#108868 12/29/03 09:30 PM
So, joemar4, to clarify:
This install did, in fact, require fuses, and somebody (previously) had deliberately eliminated them?
Even if the fuses were not required, obviously copper tubing is not listed for such a use.
Does "dummy" refer to the fuses, or...never mind...
P. S. Under the voltages/amps in this case, would said copper tubing act as a fuse or would it survive a short?
P. P. S. Is the tubing the same as what appears at the bottom-left of the top photo?
#108869 01/04/04 02:28 PM
Obviously, the plumber has been scabbing electrical work again! [Linked Image]
#108870 01/05/04 11:13 PM
DougW:
I didn't want to "go there..."
That sure would explain it, though. The fuses blew and the plumber needed to get the thing working again, and...
#108871 01/16/04 02:59 PM
I cannot determine if it is required that this disconnect be fused; there may be fuses at the starter.