His business card is in the bottom of the panel, but we must protect the identity of the guilty as well as the innocent , another thing that is a problem is a lack of circuit directories in the panels.
Do we see at least two breakers with green wires tapped off them???
Hopefully they are re-identified at the other end?!?!?!
DIY'er? Or, colorblind person did the wiring?
"Green only as grounding conductor"-what is the code article? 310.12 Conductor Identification (C) Ungrounded Conductors? ("...shall be... clearly distinguishable from grounded and grounding conductors.")
Rollie, There's not a lot of space between the breaker terminals and the Neutral Busbar. Mind you, this picture just proves that those that usually use hammers, shouldn't use screwdrivers.
Why must we protect the identity of the guilty? As a homeowner, I'd like to know who NOT to call. I say post the business card- how else will things change?