ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 560 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#101795 05/07/03 02:10 PM
Joined: May 2003
Posts: 1
N
Junior Member
If a customer wants his home ran in pipe rather than NMD, what rules should I be aware of? Can I use shared neutrals as long as the continuity of the neutral is independant of the device connections?
Also do I have to de-rate using table-5C
although these circuits are already de-rated to 80%?

Joined: Jul 2002
Posts: 175
E
Member
You can use shared neutrals, providing -
1. the two hot wires sharing a neutral are supplied from different panel busses, and
2. all the outlets supplied from those two circuits use the same neutral, if there is more than one neutral in the conduit.

You say "these circuits are already de-rated to 80%" Is this the "continuous load" derating, for Rule 8-104? If so, you only need to derate for that or Table 5C, whichever results in the largest wire size. 8-104(6)

Ed


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5