Let's start with - is this a storable pool? Is the pump Listed for use with a storable pool? Sounds like it is a storable pool since there is no mention of bonding. If it's a pump Listed for a storable pool the cord length will put it beyond the 10' and you will be using a straight blade cap and receptacle. 680.7

Unless the manufacturer's spec out a dedicated/separate circuit you could use 210.23 and put the general purpose receptacle on the same circuit as the pump. Do the math [Linked Image]


George Little