That is the reason for the equipotential BONDING grid. Even if the pool was 24vac referenced to "something else", everything within 5 feet of the water would be 24v and you would be the bird on the wire. No current would flow through your body.

The more that gets included in your bonding grid, the bigger the safe area would be.

Large ground shifts between adjacent buildings are pretty common here in Florida anyway.