Bossman you can load a circuit 100% if you want.
That changes if the loads are continuous loads.
Receptacles are not likely to fit the NEC definition of continuous load.
Continuous Load. A load where the maximum current is expected to continue for 3 hours or more.
Do you picture a multi outlet circuit to be loaded to 20 amps for 3 hours or more?